Hot Water System Leak Detection in Blandford Forum

A hot water system leak in Blandford Forum was located using damp meter readings, thermal imaging, acoustic correlation, tracer gas, leak dye, and visual inspection, with hot water leak detection confirming the source beneath a solid floor to a precise point. Found by engineer Kyle Storkey.

Leak Located Blandford Forum 0800 731 3843
CIPHE CIPHE accredited
WIAPS WIAPS member
£5m public liability insurance

THE UK'S #1 LEAK DETECTION SPECIALISTS

Facts

LocationBlandford Forum
CountyDorset
Leak TypeHot Water Leak Detection
Property TypeResidential property
Detection MethodDamp Meter, Thermal Imaging, Acoustic Correlation, Tracer Gas, Leak Dye, Visual Inspection
OutcomeHot water pipe leak found beneath utility room floor.

Symptoms

With moisture continuing to spread and no obvious source identified after the condensate repair, a professional hot water leak detection survey was arranged. The central heating system was holding steady, pointing toward the cold or hot water supply pipework as the likely source of the ongoing damage.

Key Symptom
Water damage persisted across multiple rooms after a condensate pipe repair, with the water meter showing movement indicating an active leak.

Methods Used

thermal imaging camera screen showing cold moisture anomaly on concrete floor during leak detection survey

With the system pressurised, an electronic gas sensor was used to monitor the property for escaping gas. Large concentrations were detected at the utility room floor.

Access was made through the tile work and into the concrete slab, exposing the leak source on the hot water pipe. Leak dye was applied to the pipe to confirm the location, and opening the hot water within the property caused the leak to worsen — verifying the finding.

This type of hot water leak detection, combining tracer gas with dye confirmation, is well suited to concealed pipework beneath solid floors.

Damp Meter. Used to moisture map the affected rooms, identifying elevated readings that confirmed active dampness across multiple areas.

Thermal Imaging. Carried out to trace the layout of the pipework network beneath the structure, though no thermal anomalies indicating a leak were found.

Acoustic Correlation. Used as part of the survey approach to assess the pipework for audible leak signatures.

Tracer Gas. Introduced through the garden tap in the garage and pressurised to 2 bar, then monitored across the property to locate escaping gas at the utility room floor.

Leak Dye. Applied directly to the exposed hot water pipe to mark the leak point and confirm the source when the hot water supply was opened.

Visual Inspection. Carried out at the water meter to identify movement indicating an active leak, and at the exposed pipe to assess the leak following access through the floor.

Investigation Process

  1. 1
    Moisture Mapping

    A damp meter survey was carried out across the affected rooms, finding elevated moisture readings throughout.

  2. 2
    Thermal Imaging Survey

    Thermal imaging traced the pipework network beneath the property but found no anomalies indicating a leak location.

  3. 3
    Water Meter Inspection

    The water meter was inspected and found to be moving with no water in use, confirming an active leak on the supply pipework.

  4. 4
    Tracer Gas Introduction

    Tracer gas was introduced into the internal pipework through the garden tap in the garage and the system was pressurised to 2 bar.

  5. 5
    Electronic Gas Sensor Monitoring

    The property was monitored using an electronic gas sensor, with large amounts of escaping gas detected at the utility room floor.

  6. 6
    Floor Access and Leak Exposure

    Tiles and the concrete slab were accessed in the utility room, exposing the hot water pipe and the leak source beneath the floor.

  7. 7
    Dye Confirmation

    Leak dye was applied to the pipe and the hot water supply was opened, causing the leak to worsen and confirming the exact location.

Result & Outcome

fault identified at pinhole in corroded copper pipe with fluorescent dye confirming leak point — leak located at

For a hot water leak detection case of this nature, pinpointing the leak beneath a solid floor to a precise location means remedial work can be targeted rather than speculative. The recommendations now in place cover full strip out of the affected rooms, installation of a drying programme, and reinstatement once the structure has dried. Repair to the exposed pipe section using 15mm plastic fittings and pipe can be carried out as part of that process.

Completed by Kyle Storkey, leak detection engineer at ADI Leak Detection.